Update 19:12:
Currently we received the following information from the technical team. The UPS shortcircuited one of the three phases which is about 650A, the phase went over 1 of the sensor cables inside the UPS system those cabling and module are now melted. The datacenter has a 4 hour contract with GE, and as they were doing maintenance at the time as well, they are now replacing the defective modules from the UPS system.
Please be aware that currently the system in bypass mode and is running on electrical grid of Amsterdam. They expect to finish replacement and repairs asap, we expect this to be a couple of hours. When we receive the all clear meaning that the UPS is back and functional we will update this post.